Using a large number of values in a Vista Report
  • Using a large number of values in a Vista Report
  • SESA116857
    SESA116857
‎2018-09-06 03:12 PM
Vista Reports with more than 100 individual values (not trends)
While Vista Reports are mainly used for reports on trend logs, it is possible to display values from your Vista database. If you elect to link to a large number of values in your report it is common to receive time out errors when it tries to validate the links or polls for the entire list of values.
The way to avoid these errors and speed this process up is to change the Watch Setting property to either WATCH or ALARM for each value in your report. This will instruct Vista to monitor the point values so that the validation of values or links can be accomplished much quicker when Excel and Vista Server interact. As a reference these types of errors were experienced with reports that included 100 point values.