Using a Single IP address for multiple Modbus device numbers over TCP/IP communications
  • Using a Single IP address for multiple Modbus device numbers over TCP/IP communications
‎2018-09-06 01:47 PM
Last Updated: Administrator DavidFisher Administrator ‎2019-06-05 01:18 PM
Can more than one Modbus device be mapped to the same IP Address?
Satchwell Sigma
  • IC3 Modbus
  • TCP502
Configuration not documented in release note
More than one device can be mapped via the same IP Address.  For example the gateway.txt file can be:
1,1,3,1,1,0x0001,0,0,1  ;Modsim1 40001
2,1,3,2,1,0x0001,0,0,1  ;Modsim1 40002
3,2,3,1,1,0x0001,0,0,1  ;Modsim2 40001
4,2,3,2,1,0x0001,0,0,1  ;Modsim2 40002
5,3,3,1,1,0x0001,0,0,1  ;Modsim3 40001
6,3,3,2,1,0x0001,0,0,1  ;Modsim3 40002
7,4,3,1,1,0x0001,0,0,1  ;Modsim4 40001
8,4,3,2,1,0x0001,0,0,1  ;Modsim4 40002
OUTPUT
IP_ADDRESS_TABLE
1,10.158.72.254
2,10.158.72.254
3,10.158.72.254
4,10.158.72.254
;Do not write below this line
Note: The IC3 Modbus can only be mapped to a single IP Gateway or PC application, and it is not possible to map to two applications on the same PC.
  • Satchwell BAS & Sigma
  • 5260