Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Using Xbuilder to bind SNVTs

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using Xbuilder to bind SNVTs
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Anonymous user
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1296 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using Xbuilder to bind SNVTs

Picard Product_Support
‎2018-09-06 12:00 PM

Issue

  • How to transfer data from one device to another in Xbuilder?
  • If it is possible to bind SNVT values in through Xenta Servers?

Environment

  • Xenta Servers (Xenta 511, Xenta 527, Xenta 701, Xenta 711, Xenta 721, Xenta 731, Xenta 913)

Cause

For some reason, if a user need to transfer data from one device to another under a Xenta Server (mostly, from third party devices to third party devices without using NL220 or LonMaker), “Connection Object” feature can be used to achieve this request.

Resolution

This example is showing how to transfer a room temperature value from an IO module under a Xenta 721 to a programmed SNVT input in a Xenta 301under the same Xenta 721. Other applications should be in a similar manner.

  1. Under “System” panel, right click on the folder site. (Default name is “The site name”)

  2. Expand the connection object by clicking on the “+” button on the top left. A “From” signal and a “To” signal will be displayed as shown below.

  3. Drag and drop the value from the IO module in the “Network” Panel (in this case, it is the U1 Value) on to the “From” signal as shown below.


  4. Find the SNVT variable created in the Xenta 301. In this example, go to LON->LWNetwork->XG->DDC->SNVT->LonMarkObjects->Node_Object_1->NetworkVariables->nvi_SpaceTemp. Then drag and drop this signal onto the “To” signal as shown below.
    NOTE: Do not choose the signals under “Public Signals” folder. Those signals are NOT writable.

  5. Download the project into Xenta server, the biding should start working by this point.

NOTE: It is strongly recommended to use NL220 or LonMaker to do SNVT bindings for better and more stable performances. Large amount of connection object communications may cause Xenta servers to go offline frequently.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 11196
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of