Using STR as Setpoint Adjustment to an I/O Module
  • Using STR as Setpoint Adjustment to an I/O Module
‎2018-09-10 03:27 AM
Last Updated: Crewman ContentModerator ‎2025-08-11 04:06 AM
Example Menta Programming using a STR as Setpoint adjustment to an Xenta I/O Module
  • Adjustable 10k Thermostats
  • Menta
  • STR-102
  • STR-103
  • STR-104
  • STR-105
  • STR-106
  • STR-107
  • STR-201
  • STR-202
  • STR-203
Interfacing a STR to Xenta I/O
Program an Analog Input to a Universal Input of an I/O Module
Click on the HFB above to download this .MTA file.
The Expression Block is taking the hard coded -9 to 9 input and making it adjustable from the front end.
In simulation with a Calibrated Range of 5 the following setpoint results are produced:
Analog In -9 -8 -7 -6 -5 -4 -3 -2 -1 0 1 2 3 4 5 6 7 8 9
Setpoint -2.5 -2.2 -1.9 -1.6 -1.3 -1.1 -0.8 -0.5 -0.2 0 0.2 0.5 0.8 1.1 1.3 1.6 1.9 2.2 2.5
Note: This example is for a non-linear input, with a setpoint adjust of +/-9.
For a metric calculation, use a setpoint adjust of +/-5  and change the calculation in the expression block to A*B/10