Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Using Relative linking when creating Graphics

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using Relative linking when creating Graphics
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Derrick_Ratliff
    Derrick_Ratliff
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1290 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using Relative linking when creating Graphics

Picard Product_Support
‎2018-09-06 12:53 PM

Issue

Unable to move graphics to a different drive.

Environment

I/NET Graphics Editor

Cause

When using the full path for links between I/NET graphics pages, the exact path must be preserved in order for the link to work.  If the graphics are every moved to a new PC or new location, the exact graphic path, including the drive letter must remain unchanged. 

A simple process can prevent this extra work from being required, and allow graphics to be moved freely between machines and hard drives.

Resolution

Setup -

  1. Create a root graphics folder.  Label it "Graphics" or anything you like.
  2. Create a single layer of sub-folders to help you organize graphics. (i.e. "Floor Plans" "Building1" "bmp images" etc.)
  3. If you are working on an existing system, you obviously cannot move everything to a new location, but at least try to establish a root graphics folder moving forward.

Linking

  1. Create a new graphics page called Home.gpg in the Graphics folder
  2. Edit Home.gpg
  3. Create a new link between pages by using the Page Marker tool and clicking
  4. Click on the "Select" button next to Destination page to choose the page you wish to link to
  5. A default absolute path will show up. For this example I'll link to C:\Program Files\INET Seven\Graphics\floorplan.gpg
  6. To use relative linking I have to know that both the graphic I am editing and the one I am liking to are in the same folder C:\Program Files\INET Seven\Graphics.  So in this case, I can change the link from "C:\Program Files\INET Seven\Graphicsfloorplan.gpg" to "floorplan.gpg"
  7. If I wanted to link to a page in sub-folder, for example C:\Program Files\INET Seven\Graphics\building1\VAVs.gpg, I would just change the link to "building1\VAVs.gpg"
  8. In order to link from VAVs.pgp to Home.pgp, I would have to edit the VAVs.gpg and use link with the text ..\home.gpg.  The ..\ tells the computer to look up one directory.
  9. In order to link from C:\Program Files\INET Seven\Graphics\building1\VAVs.gpg to C:\Program Files\INET Seven\Graphics\building2\AHUs.gpg, I would have to use the link "..\building2\AHUs.gpg". This tells the computer to look up one directory, then go into the building2 folder and find the AHUs.gpg

Once all graphics are set to use relative linking instead of absolute, only the self contained folder structure within the graphic folder has to stay the same. Everything can be zipped and moved to any other drive.

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 7057
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore