Using ETR-1xx sensor with Xenta controllers
  • Using ETR-1xx sensor with Xenta controllers
  • SESA116857
    SESA116857
‎2018-09-06 01:19 PM
Slide stat or temperature offset values are incorrect when using a ETR-1xx sensor with Xenta 100 or Xenta programmable controllers.
ETR-1xx
Xenta 100
Xenta 280, 300, 4xx
Similar to the STR-1xx line of sensors, there is a jumper that must be set depending on the controller the sensors is being connected to. This jumper removes or adds an extra resistor to the temperature offset value.
Set the Jumper position according to the type of controller the sensor is connected to:
Controller Jumper Position
Xenta 100 J1
Xenta Programmable J2
  • 6136