Using Absolute and nviEffectiveStpt together on a STR-350
  • Using Absolute and nviEffectiveStpt together on a STR-350
  • Anonymous user
‎2018-09-06 02:25 PM
In some situations, the STR-350 is needed to send an absolute setpoint to another device on the network, and the nviEffectiveStpt is needed to be able to raise or lower that setpoint over the network. When doing this, the nvoSetpoint will not mirror the set value in the nviEffectiveStpt.
STR-350 v1.2 & v1.3
If the nciSendHeartbeat is greater than 0, the stat will only use the adjusted value at the stat and will ignore a network value from the nvi.
Set the nciSendHeartbeat to 0 and any change on the nviEffectiveStpt will be reflected on the nvoSetpoint and as the current setpoint on the stat.
Tags (2)
  • 4020
  • thermostat