Issue
Clarification needed on whether AC-1A door modules are supported in Security Expert.
Product Line
EcoStruxure Security Expert
Environment
- SP-AC1 Controller
- Andover Continuum door modules:
- AC-1
- AC-1 Plus
- AC-1A
Cause
The AC-1A door module is not explicitly listed in the Continuum Transition documentation, leading to uncertainty about its compatibility.
Resolution
Although the AC-1A door module is not specifically mentioned in the documentation, it is supported by the Continuum Transition Tool.
This means it can be used with Security Expert when transitioning from a Continuum system.
For detailed transition steps, refer to the Continuum Transition documentation available on the Schneider Electric Exchange portal.