Xenta Server
Setting up User rights on a Xenta Server
Web Users:
  • Web Users are created only from the Web Interface, not XBuilder
  • The limitation on web users is based only on available controller memory
  • A normal user should use less than 100 bytes
  • Excess numbers of users will limit your potential use of controller memory
Simultaneous Users:
  1. In XBuilder, click on the Xenta Server object
  2. Scroll down to TCP/IP Settings and select "Max. number of HTTP sessions"
  3. the default if 15, but this number can be modified to between 10 and 20 users.
FTP Users:
  2. Scroll down to FTP settings and select "Max Users"
  3. The default number is 4, and the maximum is 5 users.