Use BACnet Enabled ABB Variable Frequency Drives with Continuum

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Use BACnet Enabled ABB Variable Frequency Drives with Continuum
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Dave_Shore
    Dave_Shore
  • LeeCravens
    LeeCravens
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4594 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Use BACnet Enabled ABB Variable Frequency Drives with Continuum

Picard Product_Support
‎2018-09-06 01:43 PM

Issue

How to Set Up BACnet Enabled ABB Variable Frequency Drives for Use With Continuum

Product Line

Andover Continuum, Other

Environment

  • ABB Variable Frequency Drives
  • Continuum

Cause

ABB VFDs must wired and configured properly to be used with a BACnet Continuum network.

Resolution

When wiring an ABB drive up to the Continuum BACnet MSTP network make the following connections:

Terminal X2

Type (+) (-) Reference
Drive Only 29 30 31
Bypass 27 28 29

 ABB recommends that when using a two conductor cable with shield that the shields not be connected  to any pin (Note that pin 29 would be unused) but simply connected together with a wire nut. However, they do say that the shields can be connected to pin 29 if the drive communication is intermittent. 

  • If the ABB drive does not have an E-Clipse bypass (E-Clipse is the ABB brand name for the bypass portion of the VFD) use the following settings:
 Parameter  Setting Notes

9802

 BACNET  Sets the communications protocol of the VFD.
5302  MAC ID Create a unique ID. A good practice is to set this to the Infinet ID + 1000. For example, if the Infinet ID is 5 then set this to 1005.

5303

 Baud Rate

 Set the baud rate being used on your BACnet network.

5311

 Device Instance ID                   This is the Infinet ID and should be set to an available number between 1-127. This will display as a hexadecimal value in the BACnet side of Cyberstation.

1001

 COMM  Set this if you want to start & stop the VFD over BACnet.

1103

 COMM  Set this if you want to control the drive speed over BACnet.

1604

 COMM  Set this if you want to reset VFD faults over BACnet.
  • If the ABB drive does include a bypass the following settings must all be entered (notice that 5302 and 5311 are now specific to the VFD portion of the unit whereas the 5002 and 5011 are specific to the bypass portion) All of these parameters as well as the parameters listed above must be entered at the bypass.
Parameter Setting Notes

5302

 Drive MAC ID  Create a unique ID specific to the VFD.

5311

 Drive Device Instance ID  This is the Infinet ID specific to the VFD.

5002

 Bypass MAC ID  Create a unique ID specific to the bypass.

5011

 Bypass Instance ID  This is the Infinet ID specific to the bypass.

NOTE
If the ABB drive is ACH550. Then the parameter below need to be set as a minimum. Other points will also need to be set depending on your site requirements, but the ones below will get communications up and running

 

 Parameter 

Setting

Notes

5301

  x5xx

-This parameter indicates the active protocol and its revision. It should read x50xx if BACnet is properly loaded. If this is not the case, confirm that drive parameter 9802 = BACNET (5).

5302

 MAC ID

-This parameter sets the drive’s BACnet MS/TP MAC ID. A temporary value of 0 places the protocol channel in reset.

5303

 Baud Rate

-Set the baud rate being used on your BACnet network.

5304

Set to 0

-This parameter sets the BACnet MS/TP character format as follows: 0 = 8N1 1 = 8N2 2 = 8E1 3 = 8O1.

5311

EFB PAR 11

 - Instance ID part1
This parameter, together with parameter 5317, EFB PAR 17, sets BACnet instance IDs: • For the range 1 to 65,535: This parameter sets the ID directly (5317 must be 0). For example, the following values set the ID to 49134: 5311 = 49134 and 5317 = 0. • For IDs > 65,535: The ID equals 5311’s value plus 10,000 times 5317’s value. For example, the following values set the ID to 71234: 5311 = 1234 and 5317 =7

5317

EFB PAR 17

 - Instance ID part2
This parameter works with parameter 5311 to set BACnet instance IDs. See parameter 5311.

1001

 COMM

-Set this if you want to start & stop the VFD over BACnet.

1103

 COMM

-Set this if you want to control the drive speed over BACnet.

1604

 COMM

-Set this if you want to reset VFD faults over BACnet.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 5371
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of