Issue
How to Set Up BACnet Enabled ABB Variable Frequency Drives for Use With Continuum
Product Line
Andover Continuum, Other
Environment
- ABB Variable Frequency Drives
- Continuum
Cause
ABB VFDs must wired and configured properly to be used with a BACnet Continuum network.
Resolution
When wiring an ABB drive up to the Continuum BACnet MSTP network make the following connections:
Terminal X2
Type | (+) | (-) | Reference |
Drive Only | 29 | 30 | 31 |
Bypass | 27 | 28 | 29 |
ABB recommends that when using a two conductor cable with shield that the shields not be connected to any pin (Note that pin 29 would be unused) but simply connected together with a wire nut. However, they do say that the shields can be connected to pin 29 if the drive communication is intermittent.
- If the ABB drive does not have an E-Clipse bypass (E-Clipse is the ABB brand name for the bypass portion of the VFD) use the following settings:
Parameter | Setting | Notes |
9802 |
BACNET | Sets the communications protocol of the VFD. |
5302 | MAC ID | Create a unique ID. A good practice is to set this to the Infinet ID + 1000. For example, if the Infinet ID is 5 then set this to 1005. |
5303 |
Baud Rate |
Set the baud rate being used on your BACnet network. |
5311 |
Device Instance ID | This is the Infinet ID and should be set to an available number between 1-127. This will display as a hexadecimal value in the BACnet side of Cyberstation. |
1001 |
COMM | Set this if you want to start & stop the VFD over BACnet. |
1103 |
COMM | Set this if you want to control the drive speed over BACnet. |
1604 |
COMM | Set this if you want to reset VFD faults over BACnet. |
- If the ABB drive does include a bypass the following settings must all be entered (notice that 5302 and 5311 are now specific to the VFD portion of the unit whereas the 5002 and 5011 are specific to the bypass portion) All of these parameters as well as the parameters listed above must be entered at the bypass.
Parameter | Setting | Notes |
5302 |
Drive MAC ID | Create a unique ID specific to the VFD. |
5311 |
Drive Device Instance ID | This is the Infinet ID specific to the VFD. |
5002 |
Bypass MAC ID | Create a unique ID specific to the bypass. |
5011 |
Bypass Instance ID | This is the Infinet ID specific to the bypass. |
NOTE
If the ABB drive is ACH550. Then the parameter below need to be set as a minimum. Other points will also need to be set depending on your site requirements, but the ones below will get communications up and running
Parameter |
Setting |
Notes |
5301 |
x5xx |
-This parameter indicates the active protocol and its revision. It should read x50xx if BACnet is properly loaded. If this is not the case, confirm that drive parameter 9802 = BACNET (5). |
5302 |
MAC ID |
-This parameter sets the drive’s BACnet MS/TP MAC ID. A temporary value of 0 places the protocol channel in reset. |
5303 |
Baud Rate |
-Set the baud rate being used on your BACnet network. |
5304 |
Set to 0 |
-This parameter sets the BACnet MS/TP character format as follows: 0 = 8N1 1 = 8N2 2 = 8E1 3 = 8O1. |
5311 |
EFB PAR 11 |
- Instance ID part1 |
5317 |
EFB PAR 17 |
- Instance ID part2 |
1001 |
COMM |
-Set this if you want to start & stop the VFD over BACnet. |
1103 |
COMM |
-Set this if you want to control the drive speed over BACnet. |
1604 |
COMM |
-Set this if you want to reset VFD faults over BACnet. |