Upgrading a 779703 bin file from a pre-I/NET Seven release to current

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Upgrading a 779703 bin file from a pre-I/NET Seven release to current
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Derrick_Ratliff
    Derrick_Ratliff
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1016 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Upgrading a 779703 bin file from a pre-I/NET Seven release to current

Picard Product_Support
‎2018-09-06 12:33 PM

Issue

Upgrading a 779703 bin file from a pre-I/NET Seven release to current.

Station conflict errors occur after upgrading a 779703 ICI

Environment

7797ICI

I/NET Seven

I/NET ICI Configurator

Cause

The 779703 ICI can be configured to use up to 4 channels using the DCU address feature HHC.  This information is then stored on the Save file. We have found that this information can be corrupted when upgrading a save file from a very old build to a very new build. The Controller will reserve the same number of addresses as configured in the MXL Panel Address.

Resolution

 

  1. Verify with the customer that it is safe to take the ICI offline
  2. Direct Connect to the ICI and perform a station save
  3. Disconnect the ICI from the controller LAN
  4. Verify that the ICI is configured as the correct type using Edit>Controller>Configuration
  5. If needed, save the controller in Network Configuration
  6. Download the bin file
  7. While the file downloads, verify it is a 779703 build
  8. Once the download is complete connect to the controller and perform a station restore
  9. Open the ICI Editor
  10. Confirm with the Fire alarm contractor that all points are monitoring correct variables
  11. Select Edit>Configuration
  12. Note the current configuration
  13. Set the ICI Port as Enabled
  14. Set the Baud Rate as 9600 – Confirm this is correct with the Fire Alarm Contractor
  15. Set the Data Bits to 7
  16. Set the Stop Bits to 1
  17. Set the Parity to Even
  18. Set the Inter message delay to .05
  19. Set the Response time out to 2
  20. Set the MXL Panel Address to 1 (this is set incorrectly intentionally on the first download after a major upgrade)
  21. Disconnect from the controller in the ICI editor
  22. In I/NET perform a station Save
  23. In I/NET perform a station restore
  24. Reconnect to the controller in the ICI Editor
  25. Change the MXL Panel Address to the correct address of the panel. This number will have to be provided by the fire alarm contractor.
  26. Use the Handheld to verify that the DPU address is correct. If the panel is 0358 this should read 005858. If 000058 then the bin file is incorrect, if 0058xx then repeat steps 20-25
  27. In I/NET perform a station Save
  28. In I/NET perform a station restore
  29. Test a point with the fire alarm system.
  30. Copy the save file to disk and save it for future reference
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 7558
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of