Issue
Upgraded to I/A Series G3 version 3.6.305 and now unable to successfully commission an MNL-800 controller. Previous versions of G3 commission the same controller without issue.
Environment
- I/A Series G3
- LonWorks module version 3.6.305
Cause
Issue with how the LonWorks module commissions a host-based controller.
Resolution
Upgrade the LonWorks module used by the I/A Series G3 station.