Upgrade to 1.5.0 or 1.6.0 fails

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Upgrade to 1.5.0 or 1.6.0 fails
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Derrick_Ratliff
    Derrick_Ratliff
  • Benji
    Benji
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2246 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Upgrade to 1.5.0 or 1.6.0 fails

Picard Product_Support
‎2018-09-11 01:58 PM

Issue

When trying to upgrade a database to version 1.5 or 1.6 the upgrade fails

Product Line

EcoStruxure Building Operation

Environment

  • Enterprise Server
  • Automation Server

Cause

There can be various reasons for the upgrade failing. At this moment there are two known issues:

  1. Issue with specific LonWorks devices such as the T-Stat T7300
  2. Too complex or long list of email addresses in notification objects

Resolution

Solution for issue 1: Issue with specific LonWorks devices such as the T-Stat T7300

Contact Product Support and ask for hotfix 1.5.0.4801


Solution for issue 2: Too complex or long list of email addresses in notification objects

  1. Make a search for all email address objects searching for "EmailAddress" - You can import this search object to do it.
  2. Copy all rows to this Excel sheet
  3. Check the "Count" column - it counts the characters in the "Property value" column. There's no exact max character count as it also depends on complexity of the addresses, but a good indicator is if the count is over 270.
  4. In SmartStruxure, delete the content of the objects having more than 270 characters.
  5. Carry out the upgrade (if the upgrade fails, go back to step 3 and delete the content of all objects where the count is 260)
  6. After upgrading copy the property content from the Excel sheet back to SmartStruxure
Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
SearchEmails.zip
EmailAddresses.zip
Tags (5)
  • Find more articles tagged with:
  • 1.4
  • 1.4.0
  • 1.4.1
  • 17053
  • tstat
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore