Unable to view TGML graphics in webstation. Get a blank screen with an error message from java console.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unable to view TGML graphics in webstation. Get a blank screen with an error message from java console.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • sesa177673
    sesa177673

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1968 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unable to view TGML graphics in webstation. Get a blank screen with an error message from java console.

Picard Product_Support
‎2018-09-06 01:49 PM

Issue

Get the following error message when viewing a TGML graphic in Webstation: 

Java-plugin 1.6.0_20
Använder JRE-version 1.6.0_20-b02 Java HotSpot(TM) Client VM
Användarens hemkatalog = C:\Documents and Settings\Administrator
----------------------------------------------------
c:   töm systemfönster
f:   slutför objekt i slutföringskö
g:   skräpinsamling
h:   visa det här hjälpmeddelandet
l:   dumpa classloader-lista
m:   skriv ut minnesförbrukning
o:   utlösarloggning
q:   dölj konsol
r:   ladda policykonfiguration på nytt
s:   dumpa system- och distributionsegenskaper
t:   dumpa trådlista
v:   dumpa trådstack
x:   töm classloader-cache
0-5: ange spårningsnivån till
---------------------------------------------------- 
PostSender: Failed to create json object: request sent is includeHidden:true, tgmlId:, requestId:3211, path:objectId=715325441&, command:GetObject, includeViewType:true, includeAggregated:0,

java.lang.NullPointerException
            at java.lang.String.indexOf(Unknown Source)
            at java.lang.String.indexOf(Unknown Source)
            at SE.Graphics.communication.TgmlGetter.checkFileIfExistsAndNotModified(TgmlGetter.java:279)
            at SE.Graphics.communication.TgmlGetter.readTgmlObject(TgmlGetter.java:374)
            at SE.Graphics.viewer.TgmlJComponent.fetchTgmlStr(TgmlJComponent.java:127)
            at SE.Graphics.viewer.TgmlJComponent.loadTgmlDocument(TgmlJComponent.java:108)
            at SE.Graphics.viewer.TgmlApplet.init(TgmlApplet.java:104)
            at sun.plugin2.applet.Plugin2Manager$AppletExecutionRunnable.run(Unknown Source)
            at java.lang.Thread.run(Unknown Source)
Undantag: java.lang.NullPointerException

or

Unable to view TGML graphics in webstation. Get a blank screen with an error message from java console.

Detected from bootclasspath: C:\PROGRA~1\Java\jre7\lib\deploy.jar
Couldn't get Int parameter debuggingPort null returning 80
Couldn't get Int parameter minPollInterval null returning 500
@TgmlApplet#init object path is: objectId=1709965313&, server path: https://system.evalvomo.fi/webstation/active.tgml?
key 0: ASP.NET_SessionId
value 0: v30z342d1nj34zwcjm1a3agu
Added cookie to result: ASP.NET_SessionId=v30z342d1nj34zwcjm1a3agu

Proxy list:[DIRECT]
proxy hosttype: DIRECT
No Proxy for this hosttype - clearing proxy settings.
executePost failed: HTTP/1.1 404 Not Found
proxy hosttype: DIRECT
No Proxy for this hosttype - clearing proxy settings.
executePost failed: HTTP/1.1 404 Not Found
PostSender: Failed to create json object: request sent is includeHidden:true, tgmlId:, requestId:1734, path:objectId=1709965313&, command:GetObject, includeViewType

Environment

TAC Vista 5.1.X

Windows 2003 server

Cause

The .tgml extension has for some reason not been registered in Internet Information Services.

Resolution

  1. Confirm that the error is as described above
  2. Register the TGML extension
    1. Go to the Start Menu and select Run.
    2. Type INETMGR and click on OK - this will open the Internet Information Services (IIS) console.
    3. Locate the virtual directory Webstation (\Web Sites\Default web site\Webstation) and right click on it.
    4. Select Properties


       
    5. Click on the Configuration button.
    6. Look for the .tgml extension in the dialogue Application Configuration that opens up, under the tab Mappings.


       
    7. If the problem is as reported, .tgml should not appear in the list. Click on Add and add the .tgml extension.
    8. Click on OK on all the open dialogues and then restart IIS.
    9. Click on Edit  and verify the checkbox "Verify that file exists" is not checked.
  3. Restart webstation and confirm the TGML are now working.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5294
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of