Unable to use Calculations on a subLAN device on a 7793
  • Unable to use Calculations on a subLAN device on a 7793
  • Derrick_Ratliff
    Derrick_Ratliff
‎2018-09-06 01:10 PM
7793
I/NET
MR controllers
The 7793 does not pass data between the A and B channel. If your calculation is comparing a point on a different channel than where the calculation resides you will need to modify the sending points global level
  1. Connect to the controller
  2. Select Edit>Controller>Resident I/O
  3. Locate the Point you are using in your calculation
  4. Modify the point
  5. Set the Global Level to "LAN"
  6. Click OK
  7. Modify the point that has the calculation extension
  8. Change it to Internal
  9. Click OK
  • TAC INET