Unable to upgrade SQL log database.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unable to upgrade SQL log database.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • LeeCravens
    LeeCravens
  • sesa177673
    sesa177673
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1441 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unable to upgrade SQL log database.

Picard Product_Support
‎2018-09-10 11:18 AM

Issue

Unable to upgrade SQL log database from a pre-5.1.7 database to the new Version 2 format that is used (for new installations and optional as upgrade) in 5.1.7. Get the error message:

Test of connection successful.
Connecting to TAC Vista SQL database.
Checking SQL server version and database size.
SQL Server Version: Microsoft SQL Server 2008 R2 (SP1) .
SQL Server Edition: Developer Edition (64-bit).
Data Allocated Space: XXXXXMB.
Data Used Space: XXXXMB.
Log Allocated Space: XXXMB.
Checking TAC Vista SQL database schema version.
Checking user access.
Upgrading TAC Vista SQL database from version 1.0.0.15 to version 2.0.0.0.
Failed to execute SQL upgrade script. Error : Error 9002, line 585: The transaction log for database 'taclogdata' is full. To find out why space in the log cannot be reused, see the log_reuse_wait_desc column in sys.databases

Environment

Vista 5.1.7 SQL log database - either upgrade when installing Vista or using the SQL Database upgrade tool.

Cause

There is insufficient space for the transaction log to grow during the upgrade process.

It is important to make sure that there is enough disk space available before upgrading the TAC Vista SQL database layout. During the upgrade procedure the database will increase its size with approximately 40%. If a SQL database is upgraded in a Microsoft SQL Server 2005 Express environment the database cannot exceed 2GB in size; the upgrade will not allow it. It is possible to upgrade to a Microsoft SQL Server 2008 Express environment where the database size limit for the upgrade is 5 GB. After the upgrade is completed, this additional storage space is not consumed by any data; the additional storage space will be allocated for future data entries in the TAC Vista SQL database. The actual data in the SQL database will decrease with approximately 30% after the conversion is completed. Do not shrink the SQL database size after a conversion; doing so will cause major fragmentation.

Resolution

Firstly, confirm that there is enough disk space (at least twice the size of the log database) for the database to grow during the upgrade.

Secondly, changes the file settings for the database to allow for the increase in size during upgrade

  1. Open SQL Management Studio (download here if required) and locate the taclogdata database.
    1. Connect to TACVISTA (default) SQL instance.
    2. Expand the menu-tree and then expand the databases tree.
    3. Locate the taclogdata (default) database.
  2. Right-click on the taclogdata database and select properties.
  3. Go to the sub-property menu Files.
  4. Change the autogrowth settings for the database log file.
    1. Go to the list of database files and identify the log file (file type Log).
    2. Click the button in the field Autogrowth.
    3. Check the size given in the Restricted file growth (MB) field.
    4. Either increase this to roughly twice the size of the database to be upgraded or
    5. Click the Unrestricted File Growth radio button.
  5. Upgrade the database to Version 2 layout.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 7938
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore