Issue
Cannot update the Vista database using the Vista system plug-in when importing a Menta file.
Environment
- Vista 5.1.4
- Xenta Programmable Controllers
- Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B
- Windows 2003 Server
Cause
The object name for the "alarm control" object was misspelled in the Menta alarm block.
Resolution
The object name for "alarm control" must match the alarm control object name in the HMI. *In the example below the spelling is correct in both places.