Unable to set the nciSpaceTempOfst to a negative number in the Xenta 104-A plug-in
  • Unable to set the nciSpaceTempOfst to a negative number in the Xenta 104-A plug-in
  • Anonymous user
‎2018-09-06 01:12 PM
The Xenta 104-A plug-in limits the temperature value input between 0°F and 18°F. It is not possible to input a negative value.
Xenta 104-A Plug-In
Lonmaker 3.1 or Lonmaker 3.2
NL220
In Vista follow these steps:
  1. Navigate to the Xenta 104-A controller.
  2. Browse down to the Node Object function block and find the nciSpaceTempOfst SCPT.
  3. Type in the designed space temp offset parameter from the default 32°F value.
For example, if a -1°F offset is needed a value of 31 will need to be entered. If a +1°F offset is needed a 33 will need to be entered. 32°F represents zero offset.