Issue
Unable to read any public signals from TAC Xenta 300/400/280 in a TAC Xenta 511, but SNVTs from TAC Xenta 100 controllers are fine.
Environment
- Xenta Programmables
- Xenta 511
- Xenta 100 series ASCs
Cause
The TAC Xenta 511 is not a member of the TAC Vista group.
Resolution
- Go to the System plug-in
- Choose LNS Network >Create group bindings.