Unable to make a TLS connection to local PC Niagara platform using Workbench
  • Unable to make a TLS connection to local PC Niagara platform using Workbench
  • RandyDavis
    RandyDavis
Guinan RandyDavis Guinan
‎2022-02-17 12:20 PM
on ‎2022-02-17 12:20 PM
Platform connection using TLS fails. Standard HTTP connection of port 3011 successful.
TAC IA Series.
I/A Series Enterprise Server
TLS platform connection fails immediately and throws an exception in Workbench. Note that the Niagara Daemon is running and a non-TLS HTTP connection is successful.
No station is currently running on the PC. All stations are stopped.
Example exception-
SEVERE [08:45:58 02-Sep-20 CDT][wb.shell] Error connecting to platform daemon at localhost:
GET /platformInfo
javax.baja.naming.UnresolvedException: platformssl:
A possible cause is a zero-byte file size bog file in the Daemon Home 'stations' folder.
  1. Check all of the station folders in Daemon Home, searching for any bog file that is zero bytes in size.
  2. Look for 'Config.bog.lock' files as one could be orphaned when a station running in the Niagara daemon were to stop unexpectedly, such as the system reboots suddenly or the PC is powered down.
  3. Remove all files that are zero bytes in size. Remove any 'Config.bog.lock' files.
  4. Test the TLS connection for a successful connection.
  • TAC IA Series
Tags (3)
  • n4
  • RandyDavis22
  • tridium
100% helpful (2/2)