Unable to display values from a Modbus IP device where it is using a data type of swapped Longint (32 bit).
  • Unable to display values from a Modbus IP device where it is using a data type of swapped Longint (32 bit).
‎2018-09-11 06:40 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 03:21 AM
Can't display values from a Modbus IP device where it is using a data type of swapped Longint (32 bit).
Continuum
Modbus IP XDriver (2nd Generation) v2.00012 and below
CX9680
ACX5720, ACX5740
bCX1-9640, bCX1-4040
PM9C Power Meter
Modbus IP Xdriver did not support the swapped Longint (32 bit) data type.
Support for this data type was added to the Modbus IP XDriver (2nd Generation) in v2.00018 which is available on The Exchange Download Center at the link below:
E01_0210_215 Modbus TCP driver.zip
  • 8033