Unable to display graphics from an I/A Series R2 Enterprise Server or UNC.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unable to display graphics from an I/A Series R2 Enterprise Server or UNC.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1810 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unable to display graphics from an I/A Series R2 Enterprise Server or UNC.

Picard Product_Support
‎2018-09-06 02:19 PM

Issue

An Internet Explorer ActiveX function involving the running of Java applets used to display the I/A Series R2 graphics prevents the Java applet from executing properly.

Environment

I/A Series R2 software release 522.v2, 529 or 532

Cause

Microsoft changed the procedure by which Internet Explorer handles third party ActiveX applets, including the Java applets used in the I/A Series R2 system.  This change was applied as an update to all older versions of Internet Explorer and is included in Internet Explorer 8.

Resolution

There was a workaround provided with the R2 522.v2 release that can be used to prevent this Java applet activation issue from happening.
The update consists of adding or modifying some of the information in the station.properties files and applies to both ES based stations and UNC based stations.

1. To update the Enterprise Server / WorkPlace Pro, save and backup the station database accordingly.
While in the admin tool, open the station.properties file.  Select menu item Admin Tool -> Host -> Edit File -> System Properties.  Edit the file by adding the following text to the end of the file.   Make sure not to delete the # character as this specifies a comment line.  Save and close the system.properties file (File ->Save).

# This is used to disable the IE ActiveX activation fix. If set to
# to false, then the user will be required to click on the applet
# before he is able to interact with it (only effects IE users).
ie.activex.activation=false

2. To update the UNCs, log into the UNC using the Admin Tool and open the station.properties file.  Select menu item Admin Tool -> Host -> Edit File -> System Properties.  Edit the file by adding the following text to the end of the file. Make sure not to delete the # character as this specifies a comment line.  Save and close the system.properties file (File -> Save).

# This is used to disable the IE ActiveX activation fix. If set to
# to false, then the user will be required to click on the applet
# before he is able to interact with it (only effects IE users).
ie.activex.activation=false

Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 4269
  • ie8
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore