UltiVist/NETWORK 8000, how to remove all or parts of the E: Segment.
  • UltiVist/NETWORK 8000, how to remove all or parts of the E: Segment.
  • sesa119747
    sesa119747
‎2018-09-06 02:49 PM
NETWORK 8000
Procedure on removing a segment.
KILBRNCH is a powerful tool, before doing the following procedure, BACKUP THE DATABASE.
In an OS/2 window, go to the FI directory and type SET NOFCS=TRUE (this command turns off communications so that the KILBRNCH command will only delete the elements in the E: Segment set to 'offline'). Press Return.
After getting the x:\FI prompt back, type KILBRNCH FI (example KILBRNCH \FI\FI E:000.GCM_00.XXX_00.xxxxxxxx). This will delete (or kill) the database from that branch.
  • E: is the Segment
  • 000 is the Network ID
  • GCM_00 is the area controller number
  • XXX_00 is the LCM/ASD device type
  • xxxxxxx is the block type
After completion, go to FI directory and then type SET NOFCS=FALSE. Refresh the E: Segment.
  • TAC IA Series
  • 2979