When controlling a circuit point in the summary, the relay does not fire.
7780 Lighting Controller
 PICO Fuse on the 7780 controller may be burned out.
Check the PICO Fuse on the 7780 controller. It may be burned out and need to be replaced. Also double check the Control Description.