Troubleshooting NiagaraNetwork Pending Subscribe / Unsubscribed

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Troubleshooting NiagaraNetwork Pending Subscribe / Unsubscribed
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1506 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Troubleshooting NiagaraNetwork Pending Subscribe / Unsubscribed

Guinan RandyDavis Guinan
‎2024-10-16 06:34 AM

on ‎2024-10-16 06:34 AM

Issue

NiagaraNetwork point subscriptions get stuck constantly reporting 'Pending Subscribe' or are 'unsubscribed'.

Product Line

TAC IA Series

Environment

  • I/A Series Jace (N4/AX)
  • I/A Series Enterprise Server (Niagara Framework N4/AX)

Cause

Various configuration issues between the Jace and Enterprise sever.

Resolution

Troubleshooting 'Pending Subscribe' or 'Unsubscribed' (N4 or AX):
  • Performing 'Manual Disconnect' on the Niagara Station 'Client connection' may clear this state.
    • Perform 'Manual Disconnect' on each side of the Niagara Network connection between the two stations having issues. It is possible that one side of the Fox connection might show connected on the 'Client Connection' and the other side shows disconnected for the associated 'Server Connection'. The manual disconnect clears this state.
  • Check for multiple FOX services.
    • Typically there is only one service, though there are use cases for more than one. Sometimes the FOX service is mistakenly duplicated and both services then have the same ports, which is incorrect and causes problems. Use the ProgramService (Batch Editor) to look for 'custom object', 'fox', 'foxService'. Either delete the extra service(s) or edit the ports so to remove any conflicts.
  • Duplicate station names can cause fox problems.
    • Look at station 'Spy', 'fox', 'log index' to see all the fox connections.
    • Look for duplicate station names that have different IP addresses. Duplicate station names can cause stations to keep getting disconnected as each station fights to be connected. Duplicate stations can be caused when an integrator connects their engineering laptop to a network and they have stations running on the laptop that were engineered for that job, thus resulting in more than one instance of a station running at once. In rare instances stations were installed multiple times at a site and not renamed before installation into the next platform.
  • Fox connection getting dropped.
    • Either network issues on the LAN or duplicate stations. Or denial of service attack on the Supervisor. Wireshark can help diagnose LAN problems or have the IT person on site look at your station IP addresses. 
  • Try increasing the Request Timeout and the Socket Option Timeout in the Fox Service.
    • Make Fox wait longer before timing out on messages. It is not typically needed to modify these defaults. 
  • Regarding AX and N4 mix, make sure when an AX is connecting to an N4, the user in the N4 station, being used by the AX, must have the AXDigestScheme for the authentication scheme. 
    • The Cipher Suite Group setting in the Fox Service must be set to 'Supported' when connecting any AX version prior to 3.8u3 (3.8.311) to an N4 station via NiagaraNetwork.
  • Make sure Provisioning is correctly configured.
    • If not being used, remove it. This might be an N4 only problem, but there have been instances encountered where a station that was converted from AX to N4 was having the 'Pending Subscribe' issue due to NiagaraProvisioning being only partially configured. Provisioning not correctly configured will cause the 'Pending Subscribe' problem
 
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • RandyDavis24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore