Trend Log Values in Xenta Server are not displayed in Trend graph but there are values if you select view data.
  • Trend Log Values in Xenta Server are not displayed in Trend graph but there are values if you select view data.
  • sesa150555
    sesa150555
‎2018-09-06 02:37 PM
  • Xenta Server
  • Xenta 511, 527, 701, 711, 721, 731, 913
If the PC time and the Xenta Server times have gotten off, it may appear that there is no data for the selected time interval.
Check that you have to same date and time settings in the Xenta Server and in the PC that you are viewing the trend chart in.
  • 3462