It is not possible to select a "Trend 10K3A1" Thermistor when configuring a central or onboard IO input point.
  • Building Operation WorkStation
  • Building Operation Automation Server (AS-P) Central IO
  • Building operation Automation Server Bundled (AS-B) Onboard IO
The specific thermistor type is not available to be selected.
Configure an input as a resistive Input with reliability level, electrical scale and engineering scale set to:
  • Upper/Top: 0
  • Lower/Bottom: 587628
Then use a Function Block 10K3A1-Ohm-To-C sample program or Script program to convert from resistance to °C.
NOTE Satchwell and Trend both use 10k3A1 Thermistors but the shunt resistance used within it will vary.
10K3A1-ohm-to-C.zip