Transfer pressure values with units of inches of water between I/NET and LON with a 913/527/731.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Transfer pressure values with units of inches of water between I/NET and LON with a 913/527/731.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • Anonymous user

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1875 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Transfer pressure values with units of inches of water between I/NET and LON with a 913/527/731.

Picard Product_Support
‎2018-09-06 02:36 PM

Issue

Transfer pressure values with units of inches of water between I/NET and LON with a 913/527/731.

Environment

I/NET

Xenta 913/527/731

XBuilder

Cause

When reading pressure from LON, the value is always in metric units, Pascals, on the LON wire. When the value comes into I/NET, it will be a large, unexpected number.

Resolution

To read in a LON pressure value into I/NET:

  1. Create two internal points in I/NET.
    1. AO to receive the raw pressure value in Pascals
    2. AI to perform the conversion to inches of water
  2. Add a calculation to the AI to perform the conversion: P0*C0
    • P0 = AO created to receive the raw pressure value in Pascals
    • C0 = 0.004 to convert value from Pascals to inches of water
  3. Set the connection object in XBuilder:
    • From = LON SNVT_press
    • To = AO to receive the raw pressure value
    The AI should be reading the correct value in units inches of water.

To write a setpoint value out of I/NET to LON:

  1. Create two internal points in I/NET:
    1. AO where the user enters desired static setpoint in inches of water
    2. AO to perform the conversion to Pascals
  2. Add a calculation to the AO to perform the conversion: P0*C0
    • P0 = AO created to enter desired static setpoint in inches of water
    • C0 = 249 to convert value from inches of water to Pascals
  3. Set the connection object in XBuilder:
    • From = AO to perform the conversion
    • To = LON SNVT_press
    The SNVT should be reading the correct value in desired units.
Labels (1)
Labels:
  • TAC INET
Tags (5)
  • Find more articles tagged with:
  • 3529
  • inches of water
  • inet
  • lon
  • Transfer pressure values
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore