Tip and tricks for communication between Xenta 913 and C-Bus

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Tip and tricks for communication between Xenta 913 and C-Bus
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • sesa64461
    sesa64461

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1952 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Tip and tricks for communication between Xenta 913 and C-Bus

Picard Product_Support
‎2018-09-06 01:51 PM

Issue

How to configure Xenta 913 to talk to C-Bus devices

Environment

  • Xenta 913
  • C-Bus

Cause

C-Bus is a public protocol which is commonly used in lighting control. Xenta 913 can be configured to talk to C-Bus devices with proper settings.

Resolution

A. Device Preparation

  1. C-bus 5500PC (PC Interface) RS-232 port

        
     
  2. Xenta 913 RS-232A port



    NOTE: Communication is between Xenta913’s RS-232A port (NOT RS-485A port) and 5500PC’s RS-232 port (NOT C-Bus port).
     
  3. Communication Cable

    Xenta913
      C-Bus 5500PC, PC Interface
    RS-232A    <---------------------> RS-232
    3(TX) <---------------------> 5(RX)
    4(RX) <---------------------> 6(TX)
    5(COM) <---------------------> 4(COM)


    Above number are RJ45 jack (as shown below) pin numbers.

 

B. Configuration

  1. Configure C-Bus device with CBusToolkit. Make sure to write down the Application number and the device’s Group number which Xenta 913 needs to communicate with.
     
  2. Configure Xenta 913 in Xbuilder.
    1. Set Application number to 38 (38 is the HEX value of 56).


       
    2. In DeviceEditor
       
    • The Group number (Hex value) needs to be inputted. Such as ‘01’ in the figure below.
    • Same Group number can be inputted in different lines; however the ‘IO’ type should not be the same, such as ‘R’ and ‘W’ in below figure.
    • ON Only and OFF Only types are NOT applicable to read-only values.

 

C. Verification

  1. In Xbuilder, drag all C-Bus points onto Value page.
  2. Download Xbuilder project into Xenta 913.
  3. Login Xenta 913 webpage and check if all point are correct and can be modified.
     

D. Additional Information

Since CBusToolkit communicates with 5500PC by 5500PC’s RS-232 port, and Xenta 913 also communicates with 5500PC by 5500PC’s RS-232 port. Therefore, Only ONE device can be connected to 5500PC’s RS-232 port for CBusToolkit and Xenta 913.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5190
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore