Thermic actuator for valve VZ219 / VZ319 / VZ419
  • Thermic actuator for valve VZ219 / VZ319 / VZ419
  • SESA150559
    SESA150559
‎2018-09-06 09:46 AM
Is there any thermic actuator that can be used with the VZ*19 valves?
  • VZ219
  • VZ319
  • VZ419
  • MZ20A
  • MZ20B
In some applications, a thermic actuator is requested
Unfortunately, the only available actuators for VZ*19 valves are the MZ20A (24V, 0-10V modulating control) and MZ20B (24V and 230V, 3 Point floating control)
  • Field Devices
  • 15311
100% helpful (1/1)