The time keeps changing between the workstation and the controller.
  • The time keeps changing between the workstation and the controller.
  • ScottLeedberg
    ScottLeedberg
‎2018-09-06 03:02 PM
Continuum controllers
UTC offsets handle time zone differences between controllers and workstations and may need to be set. Also, a time synchronization program may be required to keep the times the same.
  1. Check the UTC offsets in Cyberstation Explorer.
  2. Verify that the Network UTC offset matches the Workstation's UTC offset.
  3. Check and verify you have a Time Sync program that synchronizes the time between the workstation and controller.
  • 2338