The stopwatch object in VisiSat operates erratically when set to trigger on days.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • The stopwatch object in VisiSat operates erratically when set to trigger on days.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Gary
    Gary
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1003 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

The stopwatch object in VisiSat operates erratically when set to trigger on days.

Picard Product_Support
‎2018-09-10 07:00 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-26 03:30 PM

Issue

The Stopwatch object in the VisiSat Bubbleland object list behaves erratically when configured to trigger on a daily basis. Specifically, when set to issue a pulse once per day, it may issue multiple pulses (2–3 times) within the same day.

Product Line

Satchwell MicroNet

Environment

  • VisiSat

Cause

This is due to a software/firmware error.
Note: No fix is currently planned.

Resolution

Avoid using days as the unit for the stopwatch trigger. Instead, use hours to achieve the desired timing:

  • Replace 7 days with 168 hours 

  • Replace 14 days with 336 hours

If you need to display the value as days or weeks in MicroNet View, follow these steps:


Steps to Convert and Display in MicroNet View

  1. In VisiSat:

    • Locate the Stopwatch object

    • Add the Stopwatch Rollover to the points list

    • Go to Tools > Export and export the points list to MicroNet View

  2. In MicroNet View (Development Mode / Window Maker):

    • Open the relevant window
    • Add a text field (e.g., "###") to display the value
    • Add the tag for the stopwatch rollover value
    • To display the value in weeks, append /24 to the tag name

    Example:

    TagName/24
    
  3. Using a Data Change Script:

    • Create a tag with appropriate min/max values
    • Add a data change script to convert and display the value in weeks
    • Set the "###" field to User Inputs > Analog
    • Link it to the data change tag
  4. To Set Rollover in Days:

    • Click the days set area

    • Enter the desired number of days

    • Press Return to confirm

    ⚠️ Remember: The controller stores the value in hours (e.g., 14 days = 336 hours). The conversion to days is only for display in the MicroNet View interface.

Labels (1)
Labels:
  • Satchwell MicroNet
Tags (2)
  • Find more articles tagged with:
  • 7293
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore