The status of a Lon binding states locked. How can it be changed to bound?
  • The status of a Lon binding states locked. How can it be changed to bound?
  • sesa116873_brid
    sesa116873_brid
‎2018-09-06 01:35 PM
R2, WorkPlace Pro
Binding is locked. This can be done at the time the node is learned or a network variable can be locked on the property sheet of the node.
The Network Variable bound to the link will have to be unlocked to change the link to bound.
  1. Open the device property sheet that’s associated to the locked link
  2. Select the device tab and LonProps tab.
  3. Select and expanded the Snvt that’s associated with the locked link
  4. Unselect “Locked” and click Apply.
  5. Open LonDeviceManager under LonWorkService
  6. Highlight the device and select UpLoad
  7. Check boxes: “Upload binding info”, “Add links” and “Upload config data” and click Apply
- DO NOT check “Lock existing bindings”
The link status now read bound.
  • TAC IA Series