The shadow schedule in subordinate AS-B is not following the lead Schedule in the ES
  • The shadow schedule in subordinate AS-B is not following the lead Schedule in the ES
  • Ramaaly
    Ramaaly
Lt. Commander Ramaaly Lt. Commander
‎2023-07-10 05:22 AM
on ‎2023-07-10 05:22 AM
The shadow schedule in subordinate AS-Bs is not following the lead Schedule in the ES.
When ES transitioned to occupied all of the Shadow Schedules went into Fault and did not transition, leaving the required spaces unoccupied.
  • Building Operation Automation Server Bundled
  • Building Operation Workstation
The "Gameday Schedule [Shadow-Read only]" configuration shows that the Exceptions at Priority 10 do not have names.  As such, don't have access to the 'properties'.
By detaching the server and deleting the binding to the 'Lead object', we can delete these events and the fault condition will disappear.
As a workaround, delete these exceptions from the Lead Schedule, save, and then add them back (with a name)
  • RamaAly23