Issue
The shadow schedule in subordinate AS-Bs is not following the lead Schedule in the ES.
When ES transitioned to occupied all of the Shadow Schedules went into Fault and did not transition, leaving the required spaces unoccupied.
Product Line
EcoStruxure Building Operation
Environment
- Building Operation Enterprise Server
- Building Operation Automation Server Bundled
- Building Operation Workstation
Cause
The "Gameday Schedule [Shadow-Read only]" configuration shows that the Exceptions at Priority 10 do not have names. As such, don't have access to the 'properties'.
Resolution
By detaching the server and deleting the binding to the 'Lead object', we can delete these events and the fault condition will disappear.
As a workaround, delete these exceptions from the Lead Schedule, save, and then add them back (with a name)