The "nciPowerUpDly" does not function correctly in the MNL-800.
  • The "nciPowerUpDly" does not function correctly in the MNL-800.
  • sesa116877
    sesa116877
‎2018-09-06 02:18 PM
Changing the nci_PowerUpDly value in the MNL-800 has no effect.  With the nci_PowerUpDly set to 120 seconds in the MNL-800, the outputs turned on after 10 seconds, the default setting.
WorkPlace Tech, all versions. MNL-800
The nciPowerUpDly provided in the MNL-800 does not function correctly. The design intent of the nci was to determine the time, in seconds, that must expire following a controller reset before the MN 800 hardware outputs (Digital Outputs and Analog Outputs) are activated.
Be aware that the nciPowerUpDly in the MNL-800 does not work properly, and that the outputs are delayed approximately 10 seconds, regardless of the value entered for nciPowerUpDly.
  • TAC IA Series
  • 4299