Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

The new scheduled SQL maintenance functions don't appear to defragment the events table, whilst the trendlogvalues table has been defragmented.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • The new scheduled SQL maintenance functions don't appear to defragment the events table, whilst the trendlogvalues table has ...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa177673
    sesa177673
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1603 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

The new scheduled SQL maintenance functions don't appear to defragment the events table, whilst the trendlogvalues table has been defragmented.

Picard Product_Support
‎2018-09-10 06:08 AM

Issue

The new scheduled SQL maintenance functions don't appear to defragment the events table, whilst the trendlogvalues table has been defragmented.

Environment

Vista 5.1.7

SQL 2008 R2 SP1

Cause

A Microsoft SQL Server database is prone to data fragmentation and this is also true for the new TAC Vista SQL database layout introduced. It is recommended to keep the SQL database index fragmentation level at a low level to ensure performance in the TAC Vista system.

A new feature has been added to TAC Vista Server to schedule regular maintenance tasks on the TAC Vista SQL database to prevent the index fragmentation level to obstruct performance deterioration; this feature is called SQL Maintenance.

The SQL Maintenance feature is supported for both the new and the previous database layouts and is found in the TAC Vista Server Setup tool. TAC Vista Server Setup will also display the database layout used by TAC Vista. An event will be created in the TAC Vista Workstation event log when the maintenance task starts and ends. This event is created by TAC DSS Writer Service which launches the maintenance task. If a slave node is down in a TAC Vista network these events will not be captured by the Master node.

Resolution

TAC Vista SQL Maintenance feature will only execute if the total amount of data pages exceeds 1000 for the database. Maintenance should not be run when there is a low amount of data pages in a table. The total amount of data pages for a table is found in the index properties which can be seen using Management Studio.

  1. Open SQL management studio and connect to the tacvista database instance.
  2. Locate the taclogdata (default) database and expand the database in the tree.
  3. Under tables\event\Indexes locate PK_Events(clustered) and right-click on it.
  4. In the Index properties dialogue, under Select a page, select Fragmentation. The pages property can be seen in this page.
  5. Repeat the process for tables\trendlogvalue\Indexes\PK_Trendlogvalue(Clustered).
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 7171
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore