Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

The new program interface does not match the previously defined program interface. (Subsystem: NS, #59) when commissioning a Xenta 400/300 controller.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • The new program interface does not match the previously defined program interface. (Subsystem: NS, #59) when commissioning a ...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa150555
    sesa150555
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2327 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

The new program interface does not match the previously defined program interface. (Subsystem: NS, #59) when commissioning a Xenta 400/300 controller.

Picard Product_Support
‎2018-09-06 03:06 PM

Issue

'Program interface does not match previously defined interface' when downloading/commissioning a Xenta 400/300 controller. NS, #59

Environment

  • Vista System Plugin
  • TAC Xenta Programmable Controllers
  • LonMaker/NL220

Cause

You get this error if you have 2 controllers that are using the same device template (XIF file) and one is system program version <3.5 and one is >3.5.

Typically you will get this when you are replacing an older controller or adding a new controller to an older network.

Controllers can share device template even if they have different applications as long as the are using the same SNVTs. Different types of Xenta controllers can also share the same XIF file.

Resolution

To fix the problem you have to make sure that the new controller you are adding (replacing) gets a new XIF file and it’s own template.

  1. Open the application form System plug-in by right clicking on controller and select configure-edit.
  2. To give the application a new XIF either add a “dummy” SNVT or go to device configuration and uncheck the tick box for “XIF header generated according to LonMark standard”
  3. Hit F12, select commands and generate. F12 again and save the application to the hard drive by selecting File-save as.
  4. In system plug-in, browse in the application that you just saved on the hard drive. Update TAC Network and TAC Database. If you are asked to resynchronize, do so.
  5. In Menta create a new application with just one PVR block in it. Go to the controller, connect a serial cable and download the small application that you just created.
  6. Go back to the system plug-in and download the controller.
  7. Commission in LonMaker.
Labels (1)
Labels:
  • TAC Vista
Tags (9)
  • Find more articles tagged with:
  • 2000
  • 280
  • 281
  • 282
  • 283
  • 301
  • 302
  • 401
  • 401b
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore