The global object $Eventview is missing in the TAC Vista database.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • The global object $Eventview is missing in the TAC Vista database.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Per_Sjöstrand
    Per_Sjöstrand
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1213 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

The global object $Eventview is missing in the TAC Vista database.

Picard Product_Support
‎2018-09-06 02:59 PM

Issue

The global object $Eventview is missing in the TAC Vista database.

How to recreate global objects:
$Alarmview
$Eventview

Environment

Vista Workstation

Cause

The alarm and event view global objects have been deleted or are missing.

Resolution

Login to the master server by using TAMAIN.exe (located in the TAC Vista program folder) and check if the objects are missing.
If they are, please do as follows:

Creating a Abstract object e.g. $Eventview in TAC Vista 4.3.1 and later

  1. To see the object global eventview in workstation you need to press shift+CTRL+refresh in the object window.
  2. Assuming TAC Vista is installed as default:
    C:\Program Files\TAC\TAC Vista 4.4.1\$cfg
    Find a file named objtmpl.cfg and make sure to make a copy of that file, just in case
  3. Edit the file with notepad and find the string eventview_gl, here you can see how this object is defined.
  4. Remove AB , (stands for abstract object), save and close.
  5. Open the TAC Vista database folder and open the subfolder called $thisdb.
  6. Change the name of the file TacVista.cfg, to TacVistaold.cfg
  7. Restart TAC Vista.
  8. Start the testclient (testclt.exe) in C:\Program Files\TAC\TAC Vista 4.4.1.
  9. Log in, open services, create, ID=EventView Type=eventview_gl push create.
  10. Now you have to change the name of the created object to $Eventview.
    1. In the testclient(testclt.exe) open services, access.
    2. Log in, open services, create, Enter ID=EventView.$name.
    3. Push request, now you should see the actual name in the value field.
    4. Write $Eventview in the New Value field, press poke.
  11. Reset AB for the eventview_gl object in the objtmpl.cfg (the one you removed earlier), save and close.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 2549
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of