Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

The Xenta Repeater provides signal restoration and conditioning on LON networks

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • The Xenta Repeater provides signal restoration and conditioning on LON networks
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • LeeCravens
    LeeCravens
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1410 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

The Xenta Repeater provides signal restoration and conditioning on LON networks

Picard Product_Support
‎2018-09-10 12:14 AM

Issue

  • Xenta Repeater offers signal restoration and conditioning on LON networks
  • Lon communication issues
  • Completion-event failures

Environment

  • Vista Lon Networks
  • Xenta Repeaters (Part # 007309120)

Cause

Lon Networks can suffer communications problems due to the physical length of the network and / or due to the number of devices on the network. A Xenta Repeater can help to resolve these problems and allow for a longer physical communications network and a larger number of devices to be used.

Resolution

A Xenta Repeater is a device that uses a standard Xenta 400 base and is installed in the middle of the Lon network channel and separates it into two segments. (Note: Lon channels are sections of a Lon network that are separated by a router while segments are sections of a channel that have divided using a repeater.)

One segment of the Lon channel is connected to either of the pairs of COM 1 terminals and the other segment is connected to either of the pairs of COM 2 terminals. Each Lon segment must stay within the recommended length limits as seen below:

 

Cable Max. bus length, doubly terminated bus topology (m)/(ft) Max. node-to-node length, singly term. free topology (m)/(ft) Max. length, singly terminated free topology (m)/(ft)
Belden 85102, single twisted pair  2,700 8,858 500 1,640 500 1,640
Belden 8471, single twisted pair  2,700 8,858 400 1,312 500 1,640
UL Level IV 22AWG, twisted pair  1,400 4,593 400 1,312 500 1,640
Siemens J-Y(st)Y 2x2x0.8  4-wire helical twist, solid, shielded 900 2,953 320 1,050 500 1,640
TIA568A Cat.5 24AWG, twisted pair  900 2,953 250 820 450 1,476

 

The following rules must be adhered to:

  • A maximum of 128 devices can be placed on a Lon channel
  • A maximum of 64 devices can be placed on a Lon segment
  • A channel may use up to 2 repeaters creating a maximum of 3 segments

If a router is not being used on a channel then there may only be 64 devices on that channel since the channel is made up of only one segment.

It is recommended to limit the number of devices per segment to 50 when engineering a Lon network. This will allow for some devices to be added or re-distributed as needed during installation.

The Xenta Repeater consists of two internally connected Lon transceivers, each with a transient suppression circuit.

Data packets are picked up by the transceiver on one segment and re-broadcast onto the next segment using the second transceiver. Only Lon packets are read and re-broadcast rather than simply amplifying the signal along with all of the noise on the network. This provides for a strong, clean and noise-free signal on either side of the Xenta Repeater.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5656
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore