The Mail Service in a Niagara R2 UNC station is configured correctly however the MailRecipients are not receiving emails.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • The Mail Service in a Niagara R2 UNC station is configured correctly however the MailRecipients are not receiving emails.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116873_brid
    sesa116873_brid
  • SESA116857
    SESA116857
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1600 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

The Mail Service in a Niagara R2 UNC station is configured correctly however the MailRecipients are not receiving emails.

Picard Product_Support
‎2018-09-06 12:59 PM

Issue

The Mail Service in a Niagara R2 UNC station is configured correctly however the MailRecipients are not receiving emails.

The following errors appear in a Niagara R2 UNC Standard Output Window:
ERROR: Cannot send mail [/Acme/services/MailService]
javax.mail.SendFailedException: Sending failed;
  nested exception is:
    javax.mail.SendFailedException: Invalid Addresses;
  nested exception is:
    javax.mail.SendFailedException: 550 5.7.1 Unable to relay
    at javax.mail.Transport.send0 (bytecode 611)
    at javax.mail.Transport.send (bytecode 9)
    at tridium.services.MailService.sendImpl (bytecode 29)
    at tridium.services.MailService.checkOutbox (bytecode 101)
    at tridium.services.MailService.run (bytecode 78)
    at java.lang.Thread.run (line 5)

Turning on the MailService debug feature reveals the follow errors:
DEBUG SMTP SENT: RCPT TO:
DEBUG SMTP RCVD: 550 5.7.1 Unable to relay
.
.
Invalid Addresses
johndoe@anyconmpany.net
DEBUG SMTPTransport: Sending failed because of invalid destination addresses
DEBUG SMTP SENT: RSET
DEBUG SMTP RCVD: 250 2.0.0 Resetting
DEBUG SMTP SENT: QUIT
 

Environment

Niagara R2,  UNC-510, UNC-410, UNC-520, Enterprise Server

Cause

The SMTP server is not setup to forward email. In the above error message, joedoe@anyconpany.net does not have an email account on the server, so the email is not relayed.

Resolution

The important thing to note in both error messages is the “Unable to relay” verbiage. This indicates that the SMTP server received the email from R2. However, it can not relay it to an email address if the email account is not on the server itself.

The SMTP server must be setup to relay email messages outside of its own SMTP accounts. Contact the sites IT department for assistance with this.

Note:
If an EmailRecipient is configured with multiple email addresses and if any one of the email addresses can not be relayed by the STMP server, then none of the emails will be sent. Not even an email with a valid address on the SMTP server itself.
 

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 6760
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of