The I/A Series G3 Niagara AX Lon Tunneling control panel applet will not display previously entered configuration information on a Window 7 computer.
  • The I/A Series G3 Niagara AX Lon Tunneling control panel applet will not display previously entered configuration information...
  • SESA113595
    SESA113595
‎2018-09-06 12:55 PM
When running the G3 Niagara AX Lon Tunneling  applet on a Windows 7 computer, all display fields on the LON or Serial tunnel screen are blank.  If data is entered then the form redisplayed, it comes up blank.
Microsoft Windows 7 Professional operating system.
I/A Series G3 Niagara AX Lon Tunneling  applet
Insufficient Windows permissions.
There is no direct solution to this problem with the current version of the I/A Series G3 Niagara AX Lon Tunneling control panel applet, however, there is a workaround.
  1. Open the "My computer" Windows explorer window and locate the file c:\Windows\System32\vlonax.cpl.
  2. Right-click on the vlonax.cpl file and select "Copy".
  3. Right-click on the computer desktop and select "Paste Shortcut".
  4. Rename the shortcut to "G3 LON Tunnel".
  5. Open the Windows Control Panel.  If the Windows Control Panel is configured as "View by Category", open the "View by" pulldown box and select "Large Icons".
  6. Locate and click on the "User Accounts" entry.  The "Make changes to your user account" window will open.
  7. Click on "Change User Account Control settings".
  8. Note the position of the notification slider.  If it has already been set to the lowest or second lowest setting, no change is needed.  If the slider is to "Always Notify" or Default (second position), use the mouse to move the slider to the third position.  Click [Ok] to exit the User Account Control window.
  9. (optional) If the Control Panel display was changed in step 5, above, change the "View by" selection to "View by Category"
To run the G3 LON Tunnel control panel applet from the shortcut, right-click on the shortcut and select "Run as Administrator".  The current tunneling settings will then be displayed and any changes will be properly saved.
  • TAC IA Series
  • 6873