The I/A Series G3 Modbus TCP slave device is unable to establish communications with a Modbus client requesting a unit identifier of 255.
  • The I/A Series G3 Modbus TCP slave device is unable to establish communications with a Modbus client requesting a unit identi...
  • WaynePeters
    WaynePeters
‎2018-09-11 06:30 AM
The I/A Series G3 Modbus TCP slave device is unable to establish communications with a Modbus client requesting a unit identifier of 255.  The ENC/JACE rejects the message because the Modbus TCP slave device address can only be configured with a value between 1 to 247.
I/A Series G3 (all versions)
The Modbus TCP slave device address can only be configured with a value between 1 to 247 and Workbench will generate an exception if a value outside this range is entered and saved.
Per the Modbus TCP standard, the Modbus TCP/IP Application Data Unit (ADU) takes the form of a 7 byte header (transaction identifier, protocol identifier, length field, and unit identifier) plus the protocol data unit (function code + data).
The 7 byte MBAP header includes the following fields:
  • Transaction/invocation Identifier (2 Bytes): This identification field is used for transaction pairing when multiple messages are sent along the same TCP connection by a client without waiting for a prior response.
  • Protocol Identifier (2 bytes): This field is always 0 for Modbus services and other values are reserved for future extensions.
  • Length (2 bytes): This field is a byte count of the remaining fields and includes the unit identifier byte, function code byte, and the data fields.
  • Unit Identifier (1 byte): This field is used to identify a remote server located on a non TCP/IP network (for serial bridging). In a typical Modbus TCP/IP server application, the unit ID is set to 0 or 0xFF (255), ignored by the server, and simply echoed back in the response.
The I/A Series G3 Modbus TCP slave device address can only be configured with a value between 1 to 247 and Workbench will generate an exception if a value outside this range is entered and saved.  The workaround is to configure the value as follows.
  1. Right click on the ModbusTcpSlaveNetwork and view the ModbusTcpSlaveDevice objects.
  2. Right click on the ModbusTcpSlaveDevice object and select Pin Slots.
  3. Select the Device Address slot to pin ... select OK,
  4. Create a NumericWritable and set the value to 255.
  5. Link the output of the NumericWritable to the Device Address.
  • TAC IA Series
  • 15345