Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

The Authority Access level of bindings and links on a TGML graphic changes when the graphic is edited.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • The Authority Access level of bindings and links on a TGML graphic changes when the graphic is edited.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa115370
    sesa115370
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1250 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

The Authority Access level of bindings and links on a TGML graphic changes when the graphic is edited.

Picard Product_Support
‎2018-09-06 01:21 PM

Issue

If you edit a TGML graphic whose parent folder has had its authority changed from the default, bindings and links on the graphic may not work any more.

Say you have a graphic that you only want to make accessible via a link on another graphic i.e. it should be invisible in the Folder View.  The graphic has dynamic elements that must update, setpoints that must be adjustable, and links to other graphics.

One way to achieve this is to give the Authority of the parent folder an Access level of 'None' for Everyone, thereby hiding the folder and its contents.  You then grant individual users or groups - 'System' for example - an Access level of 'Change' as you want to be able to select the graphic to edit it after it has been created.  The bindings and links on the graphic must always have a 'Change' Access level for them to update dynamically.

You log on as System to create the folder structure, graphics, bindings, links etc. - all with the default authority Access level ('Change').  You then edit the Authority for the parent folder of your graphic, giving it an Access level of 'None' for Everyone.  You leave the two checkboxes, 'Change access level on subunits' and 'Change access level on existing objects', unticked as you do not want to change the access level of the folder contents.

This works as expected.  Log on as 'Field', for example, and the folder and its contents are not visible in the Folder View.  The hidden graphic can be opened via a link from another graphic.  Once open, dynamic values update, setpoints can be adjusted and links to other graphics work.

Log back on as System to modify the graphic.  As System you are able to select the graphic from the Folder View and launch the TGML Editor.  Modify an object on the graphic (it could be some static text, not necessarily a dynamic object). Save the graphic.  At this point the TGML editor crashes with a COMException error 'Access denied'.  The changes have been saved, however.

But now, if you log on as System, Field or any other user the modified graphic does not work.  Dynamic values are not updated and any attempt to select a dynamic value or link produces an 'Access denied' error.

Environment

TAC Vista 5.1.6

Windows 7, XP 32 bit and 64 bit

Cause

Bindings and links to graphics are saved in the database as hidden object types TGML_DYN and TGML_LINK in the same folder as the graphic they belong to.  However, when they are created they inherit the authority settings of the parent folder, not the graphic.  These settings can be changed, but a peculiarity of Vista means that when the graphic is saved the authority settings of the bindings and links revert to those currently existing for the parent folder.  If this happens to be Access level 'None' the graphic will not work for any user.

Resolution

Log on as System.

 Before editing the graphic, change the authority access level of the parent folder, including its subunits and existing objects, to 'Change' for Everyone and System.

Edit the graphic, save and close the TGML editor.

Change the authority access level of the parent folder, but not its subunits and existing objects, back to 'None' for Everyone.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 6075
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of