The AX Serial Tunnel service does not initialize on a station startup.
  • The AX Serial Tunnel service does not initialize on a station startup.
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-11 02:57 PM
The AX Serial Tunnel service does not initialize on a station startup:
---------- Station Starting:   FRI JUL 11 14:02:45 2014 ----------
Tridium Niagara Station, r2.301.529.v1 [WFU_UNC06]
MESSAGE: ErrorLogService installed [/WFU_UNC06/services/ErrorLogService]
ERROR: Could not init node [/WFU_UNC06/services/IbsAsdService/AxSerialTunnel]
java.lang.NullPointerException
   at tridiumx.tunnelAx.Tunnel.doInit (bytecode 48)
   at tridiumx.ibsAsd.AxSerialTunnel.doInit (bytecode 84)
   at tridium.foundation.node.Node.init (bytecode 1)
   at tridium.foundation.prism.LoaderModule.initNodes (bytecode 26)
   at tridium.foundation.prism.Prism.initNodes (bytecode 4)
   at tridium.foundation.Station.startStation (bytecode 60)
   at tridium.foundation.Sys.boot (bytecode 27)
   at tridium.foundation.Sys.bootLocalSns (bytecode 17)
   at tridium.tools.StationMain.bootSns (bytecode 0)
   at tridium.tools.StationMain.doIt (bytecode 352)
   at tridium.tools.StationMain.main (bytecode 10)
   at java.lang.reflect.Method.invoke (Native Method)
   at tridium.nre.Nre.mainTmpl (bytecode 271)
   at tridium.nreNre.main (bytecode 1)
TAC IA Series
Niagara R2 (revision 522 or above)
The tunnelAx jar is not installed in the host UNC. The release notes for AX Tunneling in R2 do not clearly state to install the jar file in section 2.4 and 2.5 which provide install instructions; however, section 1.2 indicates the requirement of this jar file.
Install the tunnelAx jar file prior to starting the install instructions in 2.4 and 2.5.
  • TAC IA Series
  • 16474