TTS 100 Series Thermistor Sensor

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • TTS 100 Series Thermistor Sensor
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa139513
    sesa139513
  • SESA128071
    SESA128071
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3045 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

TTS 100 Series Thermistor Sensor

Picard Product_Support
‎2018-09-06 03:10 PM

Issue

TTS 100 Series Thermistor Sensor

Environment

I/NET Seven Site

Cause

Conversion coefficient is for a Thermistor for a particular controller, and can it be used with the new controllers such as MRs/Motorola and HID/Dorado card readers

Resolution

TTS100 SERIES THERMISTOR SENSORS

Dale 1M1002-C3 Curve 1

Product Support Services continues to get calls asking what the conversion coefficient is for a Thermistor for a particular controller, and can it be used with the new controllers such as MRs. Therefore we have consolidated into this Tech Tip the variety of ways the Thermistor Series Temperature Sensors can be used with Schneider Electric's current family of controllers, including wiring, controller input range and conversion coefficients for both degrees Fahrenheit and Celsius. It makes for a great quick reference. Keep it handy.

 

MR123-210(A), 430(B), 032(C), 400(D) "I/STAT PORT ONLY"
MR88 (F), MR632 (G), MR160 (H), MR88R (K) "I/STAT or UI Inputs"

Resolution
Counts

Input
Range

Read
Range

M
Slope

B
Intercept

Temperature
Range

Span

0 - 255

0 - 5 vdc

0 - 5 vdc

0.018

-148

-40 - 176°F

Normal

 

0.01

-100

-40 - 80°C

Normal

102 - 204

2 - 4 vdc

2 - 4 vdc

0.018

-148

32 - 90°F

Narrow

 

0.01

-100

0 - 32°C

Narrow

 

MR55 / 55X (J)

Resolution
Counts

Input
Range

Read
Range

M
Slope

B
Intercept

Temperature
Range

Span

0 - 255

1.5 - 4 vdc

1.5 - 4 vdc

0.018

-148

25 - 113°F

Normal

 

0.01

-100

-4 - 45°C

Normal

 

Look-up Table #1 if wired to the I/STAT Port

Look-up Table #2 if wired to one of the Universal Input -Plug a 10K in B slot

Red - Signal In, Green - Ground

I/NET 7700 SERIES CONTROLLERS

 

Accuracy: +/- 0.2 DegC @ 25 DegC, Nominal Resistance: 10,000 Ohms @ 72 DegF

Operating Range:

TSS100WJ, D1, D2, I1, I2, S1, S2,SP, SS: 32 to 158 DegF ( 0 to 70 DegC)

TSS100OA: -4 to 158 DegF ( -20 to 70 DegC )

TSS100W: 32 to 122 DegF ( 0 to 55 DegC)

Power Requirements: 5 Volts excitation via 10K Ohm Resistor

Negative Temperature Coefficient ( Dale 1M1002-C3 Curve 1 )

 

*7716 PCU, 7718 PCU, 7728 I/SITE I/O, 7756 PCU (Upper Board Only)

Resolution
Counts

Input
Range

Read
Range

M
Slope

B
Intercept

Temperature
Range

0 - 4095

0 - 5 vdc

0 - 5 vdc

-0.1

300

-40 - 230°F

 

-0.05

150

-40 -110°C

 

819C/V (10K in B slot)

Red - Signal In, Green - Ground, DegF / DegC - See LUT Chart

*7716 PCU Rev. J boards ONLY

 

7756 PCU (Lower Board Only)

Resolution
Counts

Input
Range

Read
Range

M
Slope

B
Intercept

Temperature
Range

0 - 32767

0 - 10 vdc

0 -5 vdc

0.018

-148

-40 - 230°F

 

0.01

-100

-40 -110°C

 

6553.5C/V (10K in B slot)

Red - Signal In, Green - Ground, DegF / DegC - See LUT Chart

Thermistor Sensors Look-up Table Chart

 

7716, 7718, 7728, 7756 (Upper Board)
Fahrenheit Thermistor   Celsius Thermistor
# Count Adj Count   # Count Adj Count
1 153 521   1 153 601
2 344 1062   2 344 1202
3 816 1604   3 816 1804
4 1245 1875   4 1245 2105
5 1827 2146   5 1827 2406
6 1914 2182   6 194 2446
7 2003 2218   7 2003 2486
8 2048 2236   8 2048 2506
9 2093 2254   9 2093 2526
10 2183 2290   10 2183 2566
11 2274 2326   11 2274 2606
12 2366 2361   12 2366 2646
13 2457 2397   13 2457 2686
14 2548 2433   14 2548 2726
15 2637 2469   15 2637 2766
16 2725 2505   16 2725 2806
17 2812 2541   17 2812 2845
18 2897 2577   18 2897 2885
19 3209 2756   19 3209 3084
20 3577 2934   20 3577 3283
21 3923 3293   21 3923 3681

 

7756 (Lower Board)
Fahrenheit/Celsius Thermistor
# Count Adj Count
1 128 32846
2 2048 20039
3 4096 17584
4 6144 16185
5 8192 15180
6 10240 14373
7 11264 14016
8 12288 13681
9 13312 13363
10 14336 13058
11 15360 12191
12 16384 12474
13 17408 12191
14 18432 11910
15 19456 11629
16 20480 11346
17 21504 11058
18 22528 10762
19 23552 10455
20 24576 10132
21 28624 9412
22 28672 8514
23 30720 7161
24 32640 2438
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 1825
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore