Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

TGML graphics to display "OFF" and "ON" instead of "0" and "1"

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • TGML graphics to display "OFF" and "ON" instead of "0" and "1"
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Derrick_Ratliff
    Derrick_Ratliff
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3842 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

TGML graphics to display "OFF" and "ON" instead of "0" and "1"

Picard Product_Support
‎2018-09-06 02:34 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-06-05 01:26 PM

Issue

TGML graphics to display "OFF" and "ON" instead of "0" and "1"

Product Line

EcoStruxure Building Operation, TAC Vista

Environment

TGML Graphics Editor

Cause

Data in the Vista database is stored as 0,1 but may be displayed using paired texts. Those paired texts can be set to show up on the graphic, or a unique conversion can take place in TGML.

Resolution

If you use default snippets that come provided with the editor, you have the option of displaying a value with either NumericPresentation or TextPresentation. The only real difference between the two is that TextPresentation defines the binding's behavior format as "Presentation" rather than "None." This will only display built in presentation formats -- an alarm state will show up as "Alarm" or "Normal" -- or if you've defined paired text within a binary point in the Vista database, that will show up instead of (0,1).

This does not, however, explicitly give you the option from within the Graphics Editor to convert decimal values into text. The example TGML code below describes how to take a value that is showing up as "0" and "1" and make it read instead as "OFF" and "ON."

<Text>Value
  <Bind Attribute="Content" Name="Value">
    <ConvertValue SignalEqualTo="0" AttributeValue="OFF"/>
    <ConvertValue SignalEqualTo="1" AttributeValue="ON"/>
  </Bind>
</Text>

Cut and paste this TGML code into the editor's Source view to view it in the editor. Just be sure to paste it between the opening tag and closing tag. If all you see in the Source view is one self-closing tag, that is because the page is empty. Either add separate opening and closing tags, or go back to Design view and add one object to the page to automatically split them.You can see here that a Text object has a binding associated with it. That binding's target attribute is "Content" because this will alter the content of the Text. (We could also change the text's stroke color, background color, font size, position on the page, etc., by changing our binding's target attribute.) ConvertValues underneath the binding tell the binding how to alter the Text's content. A SignalEqualTo 0 will write "OFF" to the content and a SignalEqualTo 1 will write "ON" to the content. The number of ConvertValues is not limited to only two. There could be a third one to say that a value of 2 should read "STANDBY."

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 3610
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore