Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Launch of Consumer/Home Owner registration process!
We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.

TGML Attributes: Height, Width, Background, and Stretch

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • TGML Attributes: Height, Width, Background, and Stretch
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2418 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

TGML Attributes: Height, Width, Background, and Stretch

Picard Product_Support
‎2018-09-06 01:44 PM

Issue

  • Background image is cut off when viewing TGML graphic
  • Fit the image to the background, but it does not stretch to fit when viewing the graphic
  • White bars on the side or top of live graphic

Environment

TGML

Cause

The TGML root object has a few attributes that default to:

  • Background = #FFFFFF (white)
  • Stretch = None
  • Height = 600.0
  • Width = 800.0

These may not be appropriate for the graphic being created.

Resolution

  1. In the TGML editor, navigate to the Objects pane. If the Object pane is not visible, go to View > Objects and make sure that is checked.
  2. Click on the root Tgml object.


     
  3.  Available properties are shown in the Properties pane below. If the Properties pane is not visible, go to View > Properties and make sure that is checked.


     
  4. In a pure TGML graphic, the Background color will represent the color behind all of the components. If a large background jpg or bmp image is used, the Background color will represent the color that will show up as bars on the top and right of the graphic when it is not sized perfectly to fit in the viewer's window (if Stretch is set to None).
  5. Stretch will have three different options (this is also a user defined option, this attribute merely sets the default presentation):
    1. None -- The size of the graphic in the TGML editor is preserved in the viewer's window. This may result in blocks of color on the top or right of the graphic. It may also result in sections of the graphic being cut off from the view requiring the user to scroll to view.
    2. Uniform -- The graphic is stretched to fit the larger of either the height or width of the viewer's window. The aspect ratio of the graphic is preserved. This may result in blocks of color on the top or right of the graphic.
    3. Fill -- The graphic is stretched in both the horizontal and vertical direction to fill the entire screen. This may result in a stretched or skewed presentation of the graphic.
  6. Height and Width will set the height and width of the graphic when Stretch is set to None. In a pure TGML graphic with all vectored components, the height and width are merely relative to the size of the components and aren't of great concern. However, when a background jpg or bmp image is used, the height and width should be set to match the dimensions of the background image.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5455
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore