Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

TC300 Series

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • TC300 Series
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3483 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

TC300 Series

Picard Product_Support
‎2018-09-11 03:44 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:06 AM

Issue

TC300 Series & accuracy

Environment

BMS Site

Cause

TC300 Series & accuracy

Resolution

The TC300Series-HotelApplication Stand-alone Digital FanCoil Thermostat specifications are as follows:

There are two sensors possible for the unit. An embedded sensor is NTC100K, and for the external sensor as (below picture) it is NTC10K (3950). This chart defines the NTC Sensor accuracy (not the Control Accuracy which is in the specifications above):

 


The RS-03 10k NTC Remote Sensor-3m (Meters). Sites that want to extend further than the 3m, should know that the maximum length is 20m, we don't suggest more, but doesn't mean >20m have issues. The problem depends on the Electromagnetic Interference (EMI), Compatibility (EMC) in the field. Every site is different, and it is suggested to try in the field and see if it works fine.
(When a remote sensor is connected (terminals S1 & S2) this remote sensor is automatically used. The internal sensor is ignored.)

Note:

  • TC300 thermostat supports Modbus RTU only. If you require LON, consider the SE7000 series controller.
  • TC300 series replaces the DEGA 006905432 which is obsolete as of March 2004. 
  • To control multiple fan coils with one ST300, a connection called the ST-2 is required. This expands the control up to 4 fan coils simultaneously but is not recommended since it may lead to uncomfortable temperatures in building area.

For more info, visit The Exchange with search keywords TC300. The TC300 is only listed in the EMEA and AsiaPAC market. They are not UL approved.
 

Labels (1)
Labels:
  • Field Devices
Tags (5)
  • Find more articles tagged with:
  • 13068
  • GaryMontague22
  • tc-300
  • TC300 UL
  • TC300 UL certificate
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore