Issue
TAC Xenta devices suddenly indicate that they Needs commissioning.
Product Line
EcoStruxure Building Operation.
Environment
• Building Operation Workstation
• Xenta 401
• Xenta 301
• Xenta 281
Cause
The flag "Needs commissioning" is suddenly set.
Resolution
If the property "Needs commissioning" is set, something has changed in the settings.
This could be Subnet/Node address in the Domain table, or a change in any LonWorks binding, that caused a change in the Selector, Address, and or Alias tables.
The property Needs commissioning may also be set after a TAC Vista upgrade (conversion) or similar situations.