TAC Xenta I/O modules as LonWorks device indicates offline after power restore
  • TAC Xenta I/O modules as LonWorks device indicates offline after power restore
  • RandyDavis
    RandyDavis
  • MikaelKrantz
    MikaelKrantz
Guinan MikaelKrantz Guinan
‎2021-11-01 07:58 AM
on ‎2021-11-01 07:58 AM
TAC Xenta I/O modules working as LonWorks device, indicates offline, flashes fast after power restore.
TAC Vista, EcoStruxure Building Operation
  • XENTA421A
  • XENTA451A
When the TAC Xenta I/O modules are used as Lonworks devices, this is indicated by the LED that flash once every tenth second. After a power failure, the device will indicate offline by 5 flashes per second.
The device will indicate offline until it gets an update to any nvi or nci variable.
As soon as the device gets an update on any nvi or nci, it will again start to flash once every tenth second.
This means, that if you only read variables from the device, that is, only uses its inputs, it may indicate offline until the next time the configuration is changed.
A workaround for this issue could be to just use a dummy output, that is updated regularly.